Well pump pressure setting

Discussion in 'Open Loop' started by Bostonceltics, Jun 17, 2018.

  1. Bostonceltics

    Bostonceltics New Member

    I have a climate master tranquility 22. I have an open loop using a constant pressure variable speed submersible pump. What is the ideal pressure setting for the geothermal? Is 60psi too much pressure? Will more pressure increase its heating/cooling ability?

    Thank you

    Tom
     
  2. urthbuoy

    urthbuoy Well-Known Member Industry Professional Forum Leader

    The heat pump does not care about pressure at all. It wants flow.
     
  3. waterpirate

    waterpirate Well-Known Member Industry Professional Forum Leader

    If a open loop pumping system shares the domestic water supply, or is used for lawn irrigation. A pressure reducing valve can be employed to reduce noise and friction in the heat pump.
    Eric
     
  4. Bostonceltics

    Bostonceltics New Member

    Thank you for the replies. Wouldn’t more pressure mean more gpm flow? Does more gpm through the heat pump equal more heating/cooling ability?
     
  5. Bostonceltics

    Bostonceltics New Member

    If a pressure reducing valve is the way to go, how low should I set the psi for the geo?
     
  6. waterpirate

    waterpirate Well-Known Member Industry Professional Forum Leader

    As Chris said above ^^^^ the heat pump needs gallons not pressure. We set the pressure reducing valve to 30 psi or less. The reason is to eliminate water hammer and other related high flow issues. More pressure or less does impact it's ability to perform. High pressure causes nuisance issues. not performance issues,
    Eric
     
  7. Bostonceltics

    Bostonceltics New Member

    Thanks. I like easy fixes
     