Connecticut WaterFurnace Flashing Lo Press/Comp Led light

Discussion in 'Maintenance and Troubleshooting' started by dpwct, Aug 28, 2017.

  1. dpwct

    dpwct New Member

    I have had a WaterFurnace Geo System installed for a while. All of a sudden while trying to cool (ambient temp 72 set temp 68) the red low press/Comp light is flashing. Inside Comfort Aire diagnostics is flashing 6 times - seems to indicate "Open Start Circuit". Power cycling did not solve the problem. Any suggestions on what might be wrong and how to test/fix/

    WaterFurnace Envision Split Closed Loop
    NSZ022A11AC
    1 Zone only
    Nest Wifi Gen 1Thermostat
    Location New England

    -- WaterFurnace Flashing Lo Press/Comp Led light
     
  2. engineer

    engineer Well-Known Member Industry Professional Forum Leader

    If loop water flow is confirmed within acceptable range you may need a refrigeration / HVAC tech to check system charge, subcool, and superheat.
     
  3. dpwct

    dpwct New Member

    Do you think it might be a capacitor problem
     
  4. geoxne

    geoxne Active Member Forum Leader

    This lockout indicator is not only for low pressure. It may be tripped by a compressor fault by the Confort Alert module.

    Normal procedure is to check the code off the Comfort Alert before suspecting a refrigerant charge issue. The Comfort Alert monitors amperage draw and low voltage control signals to determine if it should lockout under many certain conditions.

    Yes, it can be tripped by a bad capacitor among other things.
     
  5. engineer

    engineer Well-Known Member Industry Professional Forum Leader

    Fair point - have the cap checked.
     