TWO units on one Loop?

Discussion in 'General Discussions' started by Home Owner SIMPSON, Feb 18, 2015.

  1. Home Owner SIMPSON

    Home Owner SIMPSON New Member

    CAN I PUT IN 2 units on one loop?
    Seems to me the second unit would exact more heat out of the discharge of the 1st unit so two units should give me 7.4 efficiently !
    Anyone ever do this?

    Bob
     
  2. waterpirate

    waterpirate Well-Known Member Industry Professional Forum Leader

    It is always about your EWT and LWT. On a closed loop it could be done for a fair amount of time, but when you exert a 4 ton load on a loop that was designed for 2 tons, failure is eminent at some point. I have done what you are saying with an open loop, but never a closed loop.
    Eric
     
  3. Palace GeoThermal

    Palace GeoThermal Well-Known Member Industry Professional Forum Leader

    You would be using twice the power so no increase in efficiency
     
  4. urthbuoy

    urthbuoy Well-Known Member Industry Professional Forum Leader

    Fifty heat pumps, 1 loop (building loop) is not uncommon. But not in the configuration you are proposing.
     
    Palace GeoThermal likes this.
  5. Bergy

    Bergy Member Industry Professional Forum Leader

    Two heat pumps on a single loop should be piped like the drawing...
     

    Attached Files:

    Palace GeoThermal likes this.