Discussion in 'Maintenance and Troubleshooting' started by geopet, Oct 13, 2010.

  1. geopet

    geopet New Member

    I have a hydronic heat pump going in High Pressure lockout. The dealer told me to close 50% the in and out valves on the ground side. Doing so the pump is running, but I think is not the solution. In the manufacturer manual for HP lockout are 2 possbility: overcharged with refrigerant, or malfunction of Expansion valve and sensing bulb. Could someone help me in solving the problem?
     
  2. urthbuoy

    urthbuoy Well-Known Member Industry Professional Forum Leader

    90%

    Most of the high pressure issues we come across are flow issues:
    - short loop
    - low flow (air, small pump) on either source or load side
     
  3. geopet

    geopet New Member

    For sure is not a low flow problem. The pump was installed 2 years ago, and it worked properly till 2 month ago. If it was a problem of low flow, why is running only with the valves on the ground side closed 50%, that means only in low flow conditions?
     
  4. teetech

    teetech Member Forum Leader

    It would be prudent to check entering and leaving temperatures on both the load and source side lines at the unit.
     
  5. AMI Contracting

    AMI Contracting A nice Van Morrison song Industry Professional Forum Leader

    is this a water to water unit? we definately need to look at low side entering and leaving temps.
    are you saying that you are throttling flow to the ground loops?
    Joe
     
  6. geopet

    geopet New Member

    Friday, October 29, 2010
    Yes it is a water to water unit. The Pump model is ECONAR Hydronic GEOSOURCE 2000 GW 670 23.9KW. It works only if the groung loop flow is throttling. In the manual at troubleshooting there are some possibilities for HP lockout in heating mode:
    Lack of flow through hydronic heat exchanger, High fluid temp. in the hydronic loop, Overcharged refrigerant circuit, Expansion valve / sensing bulb malfunction.
    Where to start searching?
     
  7. teetech

    teetech Member Forum Leader

    In heating mode high source loop temps can cause HP lockout. Could be why throttling the flow helps keep things running. Before you start tearing into things I would get those temps first. Might save you a lot time and money.
     
  8. AMI Contracting

    AMI Contracting A nice Van Morrison song Industry Professional Forum Leader

    Do you cool with this system as well?
    How old is the system.
    If it works in the fashion your installer suggests it should, why are you concerned?