Discharge Well Drop Pipe

Discussion in 'Open Loop' started by Kevin, Nov 29, 2015.

  1. Kevin

    Kevin New Member

    Should there be some type of fitting on the bottom of the drop pipe in a discharge well to create a small amount of back pressure? Or something else?

    Thanks!
     
  2. urthbuoy

    urthbuoy Well-Known Member Industry Professional Forum Leader

    Yes. A foot valve to keep a column of water in the interior plumbing and to prevent possible syphoning.
     
  3. Kevin

    Kevin New Member

    Any specific type?

    Thanks!
     
  4. Kevin

    Kevin New Member

    All of the foot valves I see are for wells, so they are one way in order to allow water to be pumped out of the well. Is there a type for geothermal where the water goes out of the foot valve?
     
  5. urthbuoy

    urthbuoy Well-Known Member Industry Professional Forum Leader

    O.K. I need to step back. Are you discharging below a waterline?

    If so, you just need an interior valve on the discharge side of the heat pump (taco, belimo).

    When discharging into a sump or site drainage, we use a pressure release foot valve to hold a column of water in the discharge piping to prevent air/growth.
     
  6. Kevin

    Kevin New Member

    Yes discharging below the waterline in a dump well, 90' down
     