Ducting in our area might be 700-800 for 100 linear feet, so its not a huge part of the cost in comparison to the rest of it. If your ducting is...
I asked about it and they do not give a different rate. However, during the winter billing months you are billed half on everything over 1000 KWH,...
How close to the Quad Cities are you? I responded in the other thread, but we had Doug's Heating and AC of the Quad Cities do ours, and I couldn't...
tstolze, We were able to get it fixed, there was a jumper wire missing on the thermostat, so essentially the aux was not running at all. Nice and...
Problem fixed, needed a jumper wire between aux and emergency on the thermostat. Aux wasn't running at all, despite it registering a few amps....
I have the technical manual for our system and best I can tell the strip is 2 stage. There is a column named 'stages' and ours has a 2 by it. We...
We have a single 10 KW electric strip - GST EAL10 10 KW, which is a 2 stage heat strip. But I bought a clamp meter and did a bit of testing....
what particulars do you need to know? I have a bit of info in my testimonial and can post more. When I say 2 F bump, I mean 2 F over heat pump...
Thanks heatoldhome. I am continuing this in my other thread under 'general discussions'...
Continuing from the other thread, if a lock out had occurred, the heat pump would not start again without restarting? Is there anything else...
heatoldhome, No, I do not have a current meter, but am thinking of getting one. I will be monitoring electric meter this week with the cold...
I guess I would expect, with the rest of the system being so sophisticated, that the aux heat would be variable as well, sort of like dialing up...
I think we have two 5KW strips for a total of 10KW. Not sure on the sizing question, but the design temp for the system was -4 F.
I am fairly positive I have two 5KW strips, for a total of 10KW. I am planning to go through the manual later on. I guess the question is,...
I played around with the aux heat on our system back in November when we first got the system running, and I noticed only a 2-3 F bump in temps...
Coldest night yet last night, got down to -3 here, and winds were up a bit. The geo wasn't actually able to keep up all night, I watched the...
We finally got our November bill and I am very happy with it. Turns out that MidAmerican Energy does graduated billing rates during the winter...
Thanks for those comments AMI, they help tremendously. My system is running as it should, based on that. We are running in stage 1 nearly 80-90%...
We had a retrofit GSHP installed back at the end of August 2014 and have been absolutely loving it so far. We switched from natural gas and...
I don't really see a setting that is similar to mine, but I don't have a honeywell. The 'Temperature Control Heat' and 'Temperature Control Cool'...