I have a Bryant geothermal system and just updated the software. I noticed there is a new feature called "windup control" which (maybe?) sounds...
New observation: what it looks like to me (maybe?) is that the system isn't letting the EWT get below 30.0 degrees. When it hits 30.0, the aux...
The tech visited in early November, here are the data from that visit: Total volts 243 Total amps 9.7 Supply air temp 99 Return air temp 70 Water...
The gas furnace heats half of the lower level and part of the upper level, thermostat is downstairs. The geo heats most of the upper level and...
I only have two pipes coming into the basement, so it looks like the manifold must be outside. The ASHP kept up just fine... when it was working....
Update: increased the thermostat on the gas system, EWT recovered to 33 degrees temporarily but it now back to 30 and it's not even very cold out...
Okay, so turns out I had the wrong number stuck in my head. 150 ft/ton is what my documentation says. The bores are backfilled with bentonite,...
Location is central Indiana. What I know about the loop is that it's supposed to be 150 feet per ton = about 450 feet. They bored four holes,...
I got a 3 ton vertical loop system installed in September, so I'm new to geo. Not yet 100% sure what to expect, but when the system was sold to...