1st floor is radiant. 2nd floor is air except for our master bathroom which has radiant. I'm not sure why I need a backup furnace, but I was...
Solution Here is the solution that has been presented: Remove 6-ton Hydro-Temp unit and the DHW and radiant tanks (system was supposed to have...
Refrigerant Accumulator I e-mailed Hydro-Temp regarding this problem and their advice is to install a refrigerant accumulator in the unit. Per...
One more thing This may or may not be helpful. According to the GeoDesigner System Analysis, daily hot water use was assumed to be 70 gallons,...
I have now had a fourth compressor malfunction on my 6 ton dual compressor Hydro-Temp unit since we moved into our new construction house July 1,...
One more pic and clarification The "filter screen" I was referring to in my non-technical jargon is called, I have now learned, a "Y strainer...
two more [IMG] [IMG]
Geo Pictures I figured out how to post these. The DHW out line filter was clogged.[IMG] [IMG] [IMG] [IMG]
Chris, it looks like the way my system is configured, that there must be a flow loop between the Hydro-Temp unit and the DHW tank even during...
I am now cautiously optimistic after installation of the new compressor followed by the troubleshooting performed by both the technician from the...
Compressor Thanks for the replies so far. The new compressor will be installed this Wednesday and I am told that an engineer from the supplier...
A lot of hot water? I just take what they give me. I am not a compulsive bather with a fear of germs, but apparently my installer thought I...
Entering and leaving temperatures EWT = 56* LWT = 67* EAT = 70* LAT = 52*
Thanks, Chris, for the reply. Unlike you, I know very little about how they work, but what you say makes a lot of sense. In fact, of the three...