I use these- Geo Solar Headers http://geosolarproducts.com/about/ Each zoned fitting is 1 1/4” inlet with 3/4” outlets. The Y splitter is 2”...
Using the “L” lockout signal to break a thermostat call will cause an endless cycle of attempted restarts with control board time delays if...
ACC1 and ACC2 are “dry contacts”. This means there is no power at these terminals. They are relay switches that make contact depending on dip...
I find little carryover of heat from my systems (Verticle Bore) from summer cooling to winter heating. In my case the average ground temperature...
I assert what you perceive as "wasteful" is NOT. Yes, electric draw will increase momentarily but for a shorter period of time as your zones are...
https://www.pmmag.com/articles/97996-climatemaster-bought-by-waterfurnace-parent NIBE I believe is just a holding company that allows its...
I use the Honeywell HZ432 on all my zoned geo systems. I prefer Honeywell TH8321R with Redlink thermostats. Together I can setup and configure to...
Wow! Good on your calculation. Now I know where the 500 comes from. Universal Hydronic Formula BTUs/hr = GPM x DeltaT x 500 for pure water (or...
I respectfully disagree. A flatplate HX has micro channels that can easily foul with open loop water flow. A flateplate HX can be destroyed...
I stand by my assertion that the TurboTec coax coil is not appropriate for your application. Sizing a hydronic heat exchanger requires calculating...
I'm not quite sure what you are trying to do here. Are you trying to isolate artesian well water from the heat pump with the heat exchanger? If...
The purpose of a flush and purge is to force the air out of the closed hydronic system. Any time the system is opened, chances are that air has...
Just a thought. Before you assume having an underperforming loop, listen to SShaw in his first post. It may save you from "chasing your tail" You...
This is correct. The flow meter from Waterfurnace comes in 2 specific models. Small (3/4") and Large (1"). The Small meter is used on units under...
High refrigerant pressure while heating is most commonly caused by low or no air flow. Check your airfilter, make sure outlets and returns are not...