I have an open loop geothermal system that takes water from a deep well in the front yard of my home and discharges it into a pond located on the...
Thanks for the response. It was a 1" PVC coupling/compression fitting rated for 150psi, which we thought was more than enough for the...
I have a Bosch SM036 water geothermal HVAC system. The configuration is open loop with incoming well water that discharges downhill into a pond....
Hi. I recently had a Bosch 3 ton (SM036) geothermal unit installed. The setup is open loop "pump and dump". I'm finding that my installer was...
I'd like give you some background and additional info on this project you may find interesting (if not sad). I do wish hindsight was 20/20....
When I check the pressure with a pressure gauge on the HP inlet valve it reads 50psi at well pump start up, then reduces down to about 12psi when...
I recently had a Bosch 3-ton Open Loop (Pump and Dump) 2-stage Geothermal Heat Pump installed. My HVAC installer did not initially set up the...
Thanks for the reply and helpful info. Well water here tends to be rather sandy, in fact just as you mentioned that psi control valve did plug up...
I recently had an HVAC company install a new Open Loop (Pump and Dump) Geothermal heat pump. It is a Bosch SM036, 2 stage, 3 ton unit. The system...