Originally Posted by
Palace GeoThermal
The OP is talking about using a very compact heat exchanger that I have very serious doubts about in a pond where there is no current.
I was thinking the same. Looking at the product, there are only a few openings where water can exchange. How would you prevent it from freezing up? At the end we are sending out fluids in the pipes at sub freezing temps.
In order to have a 6 ton capacity as claimed, and to support lets say 40.000 BTU/h heat extraction, and you assume that it is exposed to 39 degree water at the bottom of the pond, and the inside of the "ball" cannot be below 32 F, you need a minimum of 11.5 gallons per minute flow through the openings, under all the circumstances, pretty much through stratification inside the ball only. I don't see that happening.......