    Heat extraction, pond dimension, Lima-1

    Hello

    Does someone knows how to determine the seize & volume of water required in a pond to ensure regeneration of extracted heat in winter conditions?

    If a pond is too small and we use a compact heat exchanger like Lima-1, does global pond temperature could cool until 32*F and then freeze completely?


    Patrick
    Thermopompes Saguenay
    Chicoutimi (QC) Canada

  2. #2
    Palace GeoThermal is online now Trade Associate GEO Member
    Industry Professional
    Join Date
    Jan 2008
    Location
    Utah
    Posts
    1,869
    Yes, you could freeze the pond.
    Dewayne Dean

    www.palacegeothermal.com
    dean@palacegeothermal.com
    http://welserver.com/WEL0114/

    We heat and cool with dirt.
    Why settle for 90% when you can have 400%

    Geothermal, the reliable renewable.
    The sun doesn't have to shine,
    The wind doesn't have to blow.

  3. #3
    waterpirate is offline Senior Member GEO Member
    Industry Professional
    Join Date
    Dec 2008
    Location
    Delmarva Penninsula
    Posts
    1,286
    Useing an exchanger that is compact in a pond that is potentially to small would not be adviseable.. I thought I read somewhere, prolly here that 1 acre in size is the bare minimum for pond size, and even then more engineering is required.
    Eric

  4. #4
    AMI Contracting is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Howell MI
    Posts
    2,092
    In my AO half acre is minimum at 8' deep.
    Depth matters as much as surface area.
    Joe Hardin
    AMI Geothermal
    "We Dig Comfort"
    www.amicontracting.com
    www.doityourselfgeothermal.com
    "You Dig Your Comfort!"

  5. #5
    docjenser is offline Senior Member Industry Professional
    Join Date
    Apr 2009
    Posts
    953
    Let say for a 6 ton loopfield we use an area of 70x100 ft (0.16 acres) for heat exchange (slinky), why do we think that a much larger area is required for a pond, where a superior medium (water) connects the pipes to warmer ground (bottom of pond)? I have used 0.2 acres ponds 6ft deep, which work great. The key is to spread the pipe out similar to a horizontal slinky.
    www.buffalogeothermalheating.com

  6. #6
    thermopat is offline Junior Member
    Join Date
    Apr 2012
    Posts
    3
    Docjenser I think your logic is good. If I have a minimum of 8' deep and enough area for laying my slinky then why it would not work?

    I think I will use 0.2 acres per 6 tons ratio.


    AMI Contracting what is "AO" ? Thank you

  7. #7
    AMI Contracting is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Howell MI
    Posts
    2,092
    Quote Originally Posted by docjenser View Post
    Let say for a 6 ton loopfield we use an area of 70x100 ft (0.16 acres) for heat exchange (slinky), why do we think that a much larger area is required for a pond, where a superior medium (water) connects the pipes to warmer ground (bottom of pond)? I have used 0.2 acres ponds 6ft deep, which work great. The key is to spread the pipe out similar to a horizontal slinky.
    True, less will do. I quoted manufacturer minimum requirement vs practical minimum. I would caution OP to know who they are dealing with if manufacturer minimums aren't complied with.
    Joe Hardin
    AMI Geothermal
    "We Dig Comfort"
    www.amicontracting.com
    www.doityourselfgeothermal.com
    "You Dig Your Comfort!"

  8. #8
    Palace GeoThermal is online now Trade Associate GEO Member
    Industry Professional
    Join Date
    Jan 2008
    Location
    Utah
    Posts
    1,869
    Quote Originally Posted by docjenser View Post
    Let say for a 6 ton loopfield we use an area of 70x100 ft (0.16 acres) for heat exchange (slinky), why do we think that a much larger area is required for a pond, where a superior medium (water) connects the pipes to warmer ground (bottom of pond)? I have used 0.2 acres ponds 6ft deep, which work great. The key is to spread the pipe out similar to a horizontal slinky.
    The OP is talking about using a very compact heat exchanger that I have very serious doubts about in a pond where there is no current.
    Dewayne Dean

    www.palacegeothermal.com
    dean@palacegeothermal.com
    http://welserver.com/WEL0114/

    We heat and cool with dirt.
    Why settle for 90% when you can have 400%

    Geothermal, the reliable renewable.
    The sun doesn't have to shine,
    The wind doesn't have to blow.

  9. #9
    docjenser is offline Senior Member Industry Professional
    Join Date
    Apr 2009
    Posts
    953
    Quote Originally Posted by Palace GeoThermal View Post
    The OP is talking about using a very compact heat exchanger that I have very serious doubts about in a pond where there is no current.
    I was thinking the same. Looking at the product, there are only a few openings where water can exchange. How would you prevent it from freezing up? At the end we are sending out fluids in the pipes at sub freezing temps.

    In order to have a 6 ton capacity as claimed, and to support lets say 40.000 BTU/h heat extraction, and you assume that it is exposed to 39 degree water at the bottom of the pond, and the inside of the "ball" cannot be below 32 F, you need a minimum of 11.5 gallons per minute flow through the openings, under all the circumstances, pretty much through stratification inside the ball only. I don't see that happening.......
    www.buffalogeothermalheating.com

  10. #10
    urthbuoy is online now Senior Member Industry Professional
    Join Date
    Dec 2008
    Location
    Kamloops, BC, Canada
    Posts
    1,258

    Water Temperature

    Cold (liquid) water gets to around 35F around here.
    Chris Koch, P.Eng.
    Shine Energy Systems Inc.
    Website

Page 1 of 2 12 LastLast

Similar Threads

  1. Trane Heat Pump locking out for a year now - still can\'t fix
    By sugerray50 in forum Geothermal Heat Pump Discussions
    Replies: 55
    Last Post: 06-22-2011, 04:59 PM
  2. pond loop design problems
    By TReepmeyer in forum Surface Water Loops
    Replies: 21
    Last Post: 02-10-2011, 12:08 PM
  3. Bypassing the heat pump?
    By cdhand in forum Geothermal Heat Pump Discussions
    Replies: 8
    Last Post: 01-27-2010, 04:13 PM
  4. Water loop design questions for zoned heat pumps
    By Jim S in forum Geothermal Heat Pump Discussions
    Replies: 7
    Last Post: 08-01-2009, 08:00 PM