    Geodesic Dome Load Calcs.

    I have a customer who is building a geodesic dome in central Florida. I normally use HVAC Calc to work out the loads, but I'm finding it very hard to get useful results on this dome. Anyone have any experience in this?
    Greewing

  2. #2
    zfink is offline Junior Member
    Join Date
    Mar 2011
    Posts
    8
    I used Wrightsoft and made tons of custom walls and other structures when I had to bid a dome house. Luckily I did not get the project as the customer was slightly nuts.

    Where are you having trouble? If you give me a specific part of it that isn't working out for you, I might be able to guide you through a work around.

  3. #3
    AMI Contracting is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Howell MI
    Posts
    2,095
    Loads frequently require us to find the area of triangles and circles, you can assign value with what you know...insulation, floor space etc.
    Joe Hardin
    AMI Geothermal
    "We Dig Comfort"
    www.amicontracting.com
    www.doityourselfgeothermal.com
    "You Dig Your Comfort!"

  4. #4
    engineer is offline Senior Member Industry Professional
    Join Date
    Dec 2008
    Location
    Jacksonville, FL
    Posts
    2,144
    Down here in Florida, walls make almost no difference as to loads so long as they are insulated to R10 or better. We only heat through about 40 degrees and cool through 20.

    That means that the difference in wall area between a box (easy to load) and a sphere (not easily dimensioned in Man J software) is trivial relative to two 800 pound load gorillas - glass and infiltration.

    So I would model the sphere as a set of boxes, but excercise particular catuion as to glass exposure direction, shading and fenestration coefficients.

    Model the roof / ceiling as approximately equal to floor area and it should be close enough.

    We all know that it makes little difference what goes on in a load calc past the first decimal place since two stage systems are available only in whole ton increments.

    Slightly oversize the ductwork and provide manual dampers to sort out any room comfort / airflow discrepancies and call it good.
    Curt Kinder

    www.greenersolutionsair.com

    Without data, you have but an opinion.
    No thing done well is as simple as it seems

Similar Threads

  1. 3 ton vs 4 ton, conflicting load calcs: PLEASSE HELP!!!
    By hren in forum Quotes and Proposals
    Replies: 28
    Last Post: 07-22-2011, 09:27 PM
  2. Geo vs. High efficiency electric furnace
    By newtogeo in forum Geothermal Heat Pump Discussions
    Replies: 114
    Last Post: 02-04-2011, 10:27 AM
  3. Wrightsoft load short form
    By Trever B in forum Geothermal Heat Pump Discussions
    Replies: 3
    Last Post: 12-24-2010, 07:55 PM
  4. Did heating/cooling load calcs for my house - lookin 4 input
    By DooRacer500 in forum Geothermal Heat Pump Discussions
    Replies: 10
    Last Post: 06-19-2009, 08:07 AM
  5. load calcs overestimate fuel consumption and other questions...(long)
    By dshilkit in forum Geothermal Heat Pump Discussions
    Replies: 6
    Last Post: 04-16-2009, 07:16 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •