Results 1 to 6 of 6

Thread: Earthlinked DX, conversation with rep

  1. #1
    gbig2 is offline Junior Member
    Join Date
    Apr 2012
    Posts
    18

    Earthlinked DX, conversation with rep

    I filled out their dealer locator form and someone contacted me just now. I've had 3 watersource guys out to the house to give estimate. I'm debating about having a DX guy come out also. It seems people are pretty negative on the DX. Here's some things he said:
    1. Even though the posted docs on their COP % show 3.6 or lower, their actual COPs are five or higher. He says my ground temp is 51 degrees so he says I can get a 5 COP at that temp. He says DX can be %25 more efficient, less pumps, etc. He says their COPs are hurt by the criteria used to test COPs, that the testing is more favorable to watersource since the testing agency or company requires the water to be 32 degrees, which is why DX shows COPs of 3.6 instead of 4.6.
    2. Warranty on loop is 20 years. I believe watersource loops are 50 years? He said they haven't had a loop leak since 1980. I said why not warranty it to 50 years then like watersource? He didn't have a very good answer to that.

    I'm debating if I should even have someone come out. The 20 year loop warranty is a deal breaker, right? Is what he says about COP's correct?

    Thanks
    Greg

  2. #2
    Mark Custis is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Cleveland, Ohio
    Posts
    2,693

    Joe Hardin

    of AMI Contracting fame is playing email tag and ignore with the DX folks you might want to look up his thread. They will not last in my AO of Ohio unless the are coating the coils in pex or HDPE.

    I can not address the testing issue. I did fight long and hard about tax credits for water to water units.

    Mark
    We move BTUH

  3. #3
    Looby is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Philly 'burbs
    Posts
    695
    Quote Originally Posted by gbig2 View Post

    He says their COPs are hurt by the criteria used to test COPs, that the testing is more
    favorable to watersource since the testing agency or company requires the water to be
    32 degrees, which is why DX shows COPs of 3.6 instead of 4.6.
    A steaming pile of Meadow McMuffins, because:

    1) The 32 degree crap is pure technobabble. DX doesn't have anything to do with water.

    2) The 32 degree requirement for water-source closed-loops is a highly UNFAVORABLE
    and very conservative test condition. It doesn't inflate COPs -- it deflates them to yield
    pessimistic, near-worst-case ratings.

    .

    One measurement is worth a thousand expert opinions.

  4. #4
    Palace GeoThermal is offline Trade Associate GEO Member
    Industry Professional
    Join Date
    Jan 2008
    Location
    Utah
    Posts
    1,872
    Quote Originally Posted by gbig2 View Post
    He says my ground temp is 51 degrees so he says I can get a 5 COP at that temp.

    Thanks
    Greg
    As soon as you start taking heat out of the ground, the temp will drop and be down to 30° or less by the end of the heating season.
    Dewayne Dean

    www.palacegeothermal.com
    dean@palacegeothermal.com
    http://welserver.com/WEL0114/

    We heat and cool with dirt.
    Why settle for 90% when you can have 400%

    Geothermal, the reliable renewable.
    The sun doesn't have to shine,
    The wind doesn't have to blow.

  5. #5
    AMI Contracting is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Howell MI
    Posts
    2,095
    Fact is 32* soil around loops hurts all systems (or I should say drops their COP), so by the same criteria water source systems would have a higher COP with higher surrounding temperatures. Further Earthlinked training encourages heavy loading to allow greater down time during ground freeze as the soil moves heat more slowly than their loops. This is not a quote but paraphrased from the comments of the Earthlinked distributor for my area who went on to say the only failed loops he'd found were had radial cuts from ground freeze caused by poor sizing.

    I also know of a system in my area that has been running since the '80s. I agree that properly installed loops will not fail any time soon. Properly installed means (among other things) avoiding soil such as Mark sees in his AO. That said not only have there been loop failures since 1980, but Earthlinked is a 5 year old product name, previously ECR, and prior to that I'm reaching, but American Geothermal or US geothermal or..... it escapes me. The product bares resemblence to the original, suggestion that it is the same manufacturer is less than candid.

    DX dealers often feel picked upon by water-source guys, and I agree that in some instances both sides deal more in emotional propaganda than rational debate. I can tell you a respected manufacturer in Canada, however, offers both products (DX and water source) which suggests they think that both are viable technologies.

    You only need to drop about 5 titles in "General geothermal heat pump discussions" to read my reservations on DX. There is little comment on the efficiency issue as I think all manufacturers exaggerate theirs. In fact I mention that virtually everyone claims rights to the crown of most efficient. The reality is operating cost differences regardless of what you buy will likely be less than $100/yr difference at 10 cents/kwh if you employ a competant installer.

    The most important questions you can ask are the ones I have there.
    First determine if you are governed by the ICC. If so.....

    "is he ignorant of the code- following the code- subject to a different code or ignoring the code?" and "why is the aggravation of selling the least popular product worth it to him". There can be very good answers to the questions, but you won't know until you ask.

    I personally do not offer DX products at this time but continue to watch with interest to see if they resolve my concerns.

    I would invite the individual offering DX to you to join us here for a healthy debate.

    joe
    Joe Hardin
    AMI Geothermal
    "We Dig Comfort"
    www.amicontracting.com
    www.doityourselfgeothermal.com
    "You Dig Your Comfort!"

  6. #6
    docjenser is offline Senior Member Industry Professional
    Join Date
    Apr 2009
    Posts
    960
    Said it before saying it again. The amount of heat you need to extract out of the ground is the same with either system, the DX now has to do it with much lesser amount of pipe and pipe surface area.
    That means that the ground cannot keep up in transferring enough heat into the pipe. In order to work at all, now the refrigerant has to get much colder to increase the delta T between ground and pipe, resulting in much higher refrigerant pressures and less efficiency. I would argue that the ground around the loops drops actually way below 32F.The test conditions do not account for that reality and actually favor DX. The published COP actually paints a nice picture than the much colder sub 32F ground temps will render in the installed system.
    www.buffalogeothermalheating.com

Similar Threads

  1. The trouble with DX..........
    By AMI Contracting in forum Geothermal Heat Pump Discussions
    Replies: 23
    Last Post: 03-03-2013, 09:47 AM
  2. Do DX systems require HFC alarm?
    By AMI Contracting in forum Geothermal Heat Pump Discussions
    Replies: 3
    Last Post: 06-06-2010, 07:51 PM
  3. Need help with ESES DX installation
    By BostonGuy in forum Geothermal Heat Pump Discussions
    Replies: 19
    Last Post: 04-22-2009, 07:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •