    Dynamic Air Cleaner

    Hello,

    We were going to have a dynamic air cleaner installed but my service company warned me that we might have a problem with the filters getting clogged too soon because we have an old WaterFurnace 3.5 Ton ATV. He assured me that it would not damage the system but might cause the system to turn off due to the air flow sensor.

    Does anyone have any experience or advise with these units and the dynamic air cleaners?

    I really appreciate any help you can give me. I don't want to make the investment if it could cause problems.

    Thanks again.

  2. #2
    engineer is offline Senior Member Industry Professional
    Join Date
    Dec 2008
    Location
    Jacksonville, FL
    Posts
    2,146
    Aggressive, overly restrictive air filters don't combine well with whole house forced air HVAC systems.

    I've never heard of "dynamic air cleaner"

    There are any number of highly questionable devices and gizmos out there being hawked as good add-on devices to HVAC systems

    Your service company is justifiably skeptical
    Curt Kinder

    www.greenersolutionsair.com

    Without data, you have but an opinion.
    No thing done well is as simple as it seems

  3. #3
    AMI Contracting is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Howell MI
    Posts
    2,095
    Have installer of air cleaner assure you that if properly maintained the filter will not take you out of the static pressures spec'd by WF.
    Joe Hardin
    AMI Geothermal
    "We Dig Comfort"
    www.amicontracting.com
    www.doityourselfgeothermal.com
    "You Dig Your Comfort!"

  4. #4
    Mark Custis is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Cleveland, Ohio
    Posts
    2,696
    We have used them for years. They are or were considered a medical device in CA. I have seen them remove environmental tobacco smoke from the air,

    One could back up planned maintenance with a static pressure measuring device.

    WF has them available re-branded.

    Mark
    We move BTUH

Similar Threads

  1. Geo & Oil Hybrid System?
    By Crandaddy in forum Geothermal Heat Pump Discussions
    Replies: 9
    Last Post: 03-31-2011, 09:23 PM
  2. Water Furnace with media air cleaner
    By PapaGeek in forum Geothermal Heat Pump Discussions
    Replies: 7
    Last Post: 07-08-2010, 12:21 PM
  3. S.W.A.G sizing units for loads
    By saeheumsong in forum Geothermal Heat Pump Discussions
    Replies: 11
    Last Post: 11-23-2009, 06:57 PM
  4. Water-2-Water & Air Handlers
    By IdahoGEO in forum Geothermal Heat Pump Discussions
    Replies: 1
    Last Post: 02-27-2009, 07:36 PM
  5. Is This a Fair Price???
    By Darius in forum Geothermal Heat Pump Discussions
    Replies: 9
    Last Post: 08-11-2008, 02:01 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •