Page 1 of 7 12345 ... LastLast
Results 1 to 10 of 68

Thread: Measuring Heat Exchanger Flow Rates?

  1. #1
    Looby is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Philly 'burbs
    Posts
    695

    Measuring Heat Exchanger Flow Rates?

    So, I bought myself a handy-dandy digital pressure gauge (plus snubber &
    P/T port adapter) to check the flow rate on my new WF Envision ND038.
    Works great, readable to 0.1 ft of head ...man I got this sucker NAILED!

    Pulled up the WF pressure drop tables with delta-P versus GPM at various
    temperatures and... OOPS! noticed that WF doesn't mention antifreeze
    corrections in conjunction with flow rate measurements. No mention in
    the ClimateMaster manuals -- and nothing obvious on TheGoogle, either.

    My first thought was to guesstimate an antifreeze correction from the loop
    piping pressure drop tables, but then noticed that the 1.25" PE pipe tables
    show a 20%-ish penalty for methanol versus water (no antifreeze) -- but
    another table for p-drop per 100' of 1" rubber hose (from ClimateMaster)
    shows virtually no difference at all between methanol and water PD's.

    Anyone have experience with this? Why the big difference in antifreeze
    effects for different kinds of pipe? Should HeatEx p-drop measurements
    be corrected for antifreeze? How much correction for 20% v/v methanol?

    BTW, my system is working very well -- except that I'd really like to
    see 2-3°F higher temps at the registers. I'm trying to get a good GPM
    measurement to see if it would be worthwhile to add a second/larger
    circ pump. A 20% difference between uncorrected and 'corrected' PDs
    is the difference between the near-optimum and bare-minimum flows
    recommended by WF.

    FWIW, I'm seeing delta-P = 6.1 ft head (2.6+ PSI) at 42°F EWT.

    ...TIA,

    Looby

    One measurement is worth a thousand expert opinions.

  2. #2
    waterpirate is offline Senior Member GEO Member
    Industry Professional
    Join Date
    Dec 2008
    Location
    Delmarva Penninsula
    Posts
    1,288
    I do not know why the penalty for methanol? Methanol is usually the fluid of choice where it is legal because it does not add viscosity which adds friction loss. Also in the world of "c" factors for pipe rubber hose is the worse. Maybe WF thought the c factor was so low allready they did not add for antifreeze.

  3. #3
    hardchines is offline Senior Member
    Join Date
    Jan 2009
    Posts
    318
    Excuse my obvious question but why not just install a flow gauge?

  4. #4
    waterpirate is offline Senior Member GEO Member
    Industry Professional
    Join Date
    Dec 2008
    Location
    Delmarva Penninsula
    Posts
    1,288
    Flow meters are a "potential" source of a problem on a closed loop system. The Pete's ports are accepted as a better way.

  5. #5
    Looby is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Philly 'burbs
    Posts
    695
    Quote Originally Posted by hardchines View Post
    Excuse my obvious question but why not just install a flow gauge?
    I didn't want to open the system, install a flow meter,
    and re-purge -- just to find out whether I should open
    the system, install a second circ pump, and re-purge.

    Also, unlike a dedicated flow meter, a digital pressure
    gauge is a handy-dandy tool with many uses (such as
    checking loop pressure) -- and it was under $100.

    As waterpirate points out, inline flow meters are a
    potential source of problems, and I have no need to
    monitor GPM continuously. Just want one 'baseline'
    initial measurement and very occasional re-checks.

    The pressure gauge gives me precise (+/- 0.1 ftwc)
    p-drop measurements -- the only problem is that I'm
    not sure how to accurately convert delta-P to GPM.

    ...the answer is out there, somewhere,

    Looby

    One measurement is worth a thousand expert opinions.

  6. #6
    hardchines is offline Senior Member
    Join Date
    Jan 2009
    Posts
    318
    I did not know that it was involved to install a flow meter so I understand your point. I run open loop so I have more variables to deal with, and I am a like to see what is going on kinda guy! I have visual flow gauges (sorta fail safe) on both units and EWT, LWT's, and HWG in and out Omaga digital
    temperature gauges so at a glance I can see what is going on. I do not push this set up as most would think it is over kill, but I like it.

  7. #7
    Mark Custis is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Cleveland, Ohio
    Posts
    2,696

    I pipe guages anywhere I can

    So I can "see the flow".

    Lobby: Look in the manual for converstion tables.
    We move BTUH

  8. #8
    waterpirate is offline Senior Member GEO Member
    Industry Professional
    Join Date
    Dec 2008
    Location
    Delmarva Penninsula
    Posts
    1,288

    Agreed

    I live and die by the bucket and stop watch for well work, but I am not sure how to apply that concept to a closed loop system that does not employ a tank?

    The rubber hose gets a bad rap on the friction loss chart when compared to other pipes c factor, that plus the viscosity reduction is a killer. I was misinformed as to the impact that methanol had in a loop system. So it is the lesser evil, but still evil?

  9. #9
    hardchines is offline Senior Member
    Join Date
    Jan 2009
    Posts
    318
    OK Loopy return your new toy and pick up a flow meter! Or a bucket!

  10. #10
    Looby is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Philly 'burbs
    Posts
    695
    Quote Originally Posted by cnygeo View Post
    I have yet to see a table from a manufacturer with these effects listed
    in enough detail to expect good accuracy.
    There's plenty of info for p-drop versus GPM versus temperature, with
    ethanol, methanol, glycol, and jus' plain water -- but only for the loop
    piping. I plotted WF's heat exchanger p-drop data for the Envision 038
    (apparently, without antifreeze) -- and also a set of curves with a 20%
    'correction' for methanol. Only problem is, I don't know whether the
    'corrected' data is better/worse than WF's uncorrected values straight
    from the tables:

    The other issue is that it assumes that the heat exchanger is perfectly clear.
    If the heat exchanger is restricted for any reason it will cause the flow to
    drop and the pressure drop to increase. So if you're checking flow by
    pressure drop, flow will appear to INCREASE as the heat exchanger becomes
    more and more restricted.
    Heat exchanger fouling shouldn't be a problem in a closed-loop system.
    Also, any significant heat exchanger blockage/restriction should show up
    as a LARGE increase in exchanger p-drop. Reduced flow will increase the
    circ pump's output pressure a bit, and reduce the loop piping's p-drop --
    so, the exchanger p-drop should rise dramatically.

    a bucket and stopwatch is a surprisingly accurate way to measure flow
    True 'nuff. Now, all I need is a 0.125" bucket that'll fit through a P/T port.

    Looby

    One measurement is worth a thousand expert opinions.

Page 1 of 7 12345 ... LastLast

Similar Threads

  1. Can loop flow rates be too high?
    By newgeohp in forum Maintenance and Troubleshooting
    Replies: 28
    Last Post: 09-04-2010, 05:14 AM
  2. rusty heat exchanger
    By cgreen in forum Geothermal Heat Pump Discussions
    Replies: 10
    Last Post: 02-16-2010, 06:46 AM
  3. Flow rates and piping help
    By DEZYNE in forum Geothermal Heat Pump Discussions
    Replies: 16
    Last Post: 04-02-2009, 08:40 PM
  4. How much heat can an exchanger take?
    By sybersmith in forum Geothermal Heat Pump Discussions
    Replies: 11
    Last Post: 03-25-2009, 09:30 AM
  5. Measuring Heat Pump Performance - Data Logger?
    By Eric D in forum Geothermal Heat Pump Discussions
    Replies: 9
    Last Post: 04-28-2008, 05:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •