Thread: Closed horizontal loop pressure

  1. #11
    teetech is offline Senior Member Industry Professional
    Join Date
    Sep 2009
    Posts
    371

    Pressure

    HE = GPM X water deta T X 485 (brine)

    There are no pressure numbers in that formula.

    Grundfos recommends 2 - 3 lbs pressure at pump inlet which is met by standing water column on a pressure-less flow center.

    I think Dewayne hit this on the head.

  2. #12
    Looby is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Philly 'burbs
    Posts
    695
    Quote Originally Posted by geome View Post
    I wouldn't mind assembling these parts, but is there any way to get more specific
    information on the P/T port adapter that I would need to connect to the other parts?
    Just those three parts, they thread together directly. Nothing else needed
    except some teflon thread-sealing tape -- available in any hardware store.

    Gauge is 1/4" NPT male, P/T probe (gauge adapter) is 1/4" NPT female.
    The (optional) snubber goes between; one end is male, the other female,
    both 1/4" NPT threads. Here are some gauge adaptor part numbers:

    Sisco model# GA-125 or Petesplug model# 520

    Or, ask your installer to get one for you -- he might have it in stock.

    good luck,

    Looby

    One measurement is worth a thousand expert opinions.

  3. #13
    docjenser is offline Senior Member Industry Professional
    Join Date
    Apr 2009
    Posts
    953
    Quote Originally Posted by teetech View Post
    HE = GPM X water deta T X 485 (brine)

    There are no pressure numbers in that formula.

    Grundfos recommends 2 - 3 lbs pressure at pump inlet which is met by standing water column on a pressure-less flow center.

    I think Dewayne hit this on the head.
    May be you misunderstood. My point for heat extraction was that the numbers indicate that the system runs very efficient wether you have a pressurized or non-pressurized system, actually above factory specs. Since waterfurnace commented that with lesser loop pressure you loose efficiency, I was doubting that this was the case and questioning why.

  4. #14
    urthbuoy is online now Senior Member Industry Professional
    Join Date
    Dec 2008
    Location
    Kamloops, BC, Canada
    Posts
    1,258

    Loop Pressurization

    Loop pressurization is to ensure air has been removed and to prevent pump cavitation on the suction side of the pump.

    I've never been an expert on pump cavitation as it can get pretty complex. Most pump manufacturers report desired minimum pressures (required head pressures). Cavitation can take place at some relatively high pressures in some cases.

    If in doubt, look up the head pressure requirements for your circulating pumps and see if they are adequate.
    Chris Koch, P.Eng.
    Shine Energy Systems Inc.
    Website

  5. #15
    WF_Inc is offline Senior Member GEO Member
    Industry Professional
    Join Date
    Jan 2010
    Location
    Fort Wayne, Indiana
    Posts
    145
    geome,

    In WaterFurnace training courses we teach that the heat of extraction/rejection should be calculated during startup and service.
    WaterFurnace International, Inc.

  6. #16
    WF_Inc is offline Senior Member GEO Member
    Industry Professional
    Join Date
    Jan 2010
    Location
    Fort Wayne, Indiana
    Posts
    145
    docjenser,

    We apologize for not specifying in our original post that the numbers provided were for a pressurized closed loop system. Non-pressurized systems are a little different. When using a non-pressurized flow center in a closed loop system, the minimum water pressure required by the circulating pump is maintained by a column of water in the cylinder above the pump. Pressures that we refer to are suggested operating pressures. Pumps used in these applications, only need 3psi or greater to function normally. Our concern is that the pressure does not drop below the minimum 3psi.
    WaterFurnace International, Inc.

  7. #17
    geome is offline Senior Member
    Join Date
    May 2009
    Location
    SW Virginia
    Posts
    849

    Closed horizontal loop pressure

    Looby & WF, thank you again for your replies.
    Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.

  8. #18
    docjenser is offline Senior Member Industry Professional
    Join Date
    Apr 2009
    Posts
    953
    Quote Originally Posted by WF_Inc View Post
    docjenser,

    We apologize for not specifying in our original post that the numbers provided were for a pressurized closed loop system. Non-pressurized systems are a little different. When using a non-pressurized flow center in a closed loop system, the minimum water pressure required by the circulating pump is maintained by a column of water in the cylinder above the pump. Pressures that we refer to are suggested operating pressures. Pumps used in these applications, only need 3psi or greater to function normally. Our concern is that the pressure does not drop below the minimum 3psi.
    Thanks for your reply.
    I understood that you meant pressurized systems, however you made a comment that you loose efficiency with lower pressure, which I questioned.
    As long as you do not suffocate the pump, which would reduce flow, efficiency should not be affected. I used the non-pressurized systems as an example. Grundfos 26-99 are used for both pressurized and non-pressurized systems, it would be new for me that they differ.

  9. #19
    Looby is offline Senior Member Industry Professional
    Join Date
    Jan 2009
    Location
    Philly 'burbs
    Posts
    695
    Quote Originally Posted by docjenser View Post
    As long as you do not suffocate the pump, which would reduce flow,
    efficiency should not be affected.
    I agree. I don't see how a heat pump could possibly know/care about
    the static pressure of the brine. GPM is GPM; delta-T is delta-T; and
    static pressure has no effect on heat capacity.

    As long as the loop circ pump isn't cavitating, I see no mechanism
    by which the static pressure of the brine could affect heat extraction,
    pumping losses, compressor load, or any other aspect of efficiency.

    One measurement is worth a thousand expert opinions.

  10. #20
    WF_Inc is offline Senior Member GEO Member
    Industry Professional
    Join Date
    Jan 2010
    Location
    Fort Wayne, Indiana
    Posts
    145
    docjenser,

    You are correct. The efficiency loss and will occur when the pressure is below 3psi. At these pressures we are concerned with air getting in the pump and causing cavitation, which then could result in pump failure. Pressure will change as the temperature changes. Our goal is to have enough pressure on the loop that it can go through the seasonal temperature changes and still maintain a positive pressure.
    WaterFurnace International, Inc.

Page 2 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. Installing Horizontal Closed Loop- Best Way
    By ciws14 in forum Geothermal Heat Pump Discussions
    Replies: 4
    Last Post: 06-19-2010, 10:10 PM
  2. calcium removal in horizontal closed loop
    By new2geo in forum Vertical and Horizontal Loops
    Replies: 6
    Last Post: 05-25-2010, 09:21 PM
  3. Horizontal Grid Closed Loop Geothermal Heat Pump Trench Size
    By Kdeclercq in forum Geothermal Heat Pump Discussions
    Replies: 20
    Last Post: 02-06-2010, 02:57 PM
  4. Is my horizontal closed loop leaking?
    By rldubrule in forum Geothermal Heat Pump Discussions
    Replies: 12
    Last Post: 03-01-2009, 03:18 PM
  5. Closed Loop Pressure New install
    By rw1995 in forum Geothermal Heat Pump Discussions
    Replies: 5
    Last Post: 11-16-2008, 10:55 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •